We work with multiple POCO's. One will have you bond the grounded conductor in the meter can, another will forbid it. My question is, if we are asked to bond the grounded conductor inside the meter can, are we still obligated to bond the grounded conductor at the main disconnect? Are we permitted to do it? Is it optional? 250.24(A)(1) seems to say it can be done at either location, to and including the the terminal or bus at the main. Am I interpreting that correctly to assume I need to still bond the neutral to the GEC at the main service disconnect?