Mike83
New member
- Location
- New jersey
I have 2 200 amp main breaker panels in a medical building that are rated for 10k each and 2 200 amp non fused Disconnect that are rated for 10 k each. The inspector wants 22k AIC rating so my question is can i replace the disconnect breaker and leave the panels at 10k? The inspector is requisition amendment letter from the site engineer which in return he needs a letter from the power company which hasn't got back to yet. Try to figure out other Options before i start getting fine bye the GC