250.24 (A) (2) requires a second neutral to grounding electrode connection where the service is supplied by an outdoor transformer. It says it shall be made at the transformer, or anywhere else outside the building. The handbook shows an example of the transformer and main service disconnect in two different locations, and shows a grounding electrode connection to two separate grounding electrodes, one being at the service, and the other at the transformer. I saw a situation with an outdoor transformer, and outdoor service disconnect, both located less than 10 feet apart. In this case, I think 250.50 would require the two grounding electrodes to be connected together, and this would cause objectionable current. How would one follow the requirements of 250.24A2 here?