I plan on sending the replies to this thread to a couple of engineers in my area that I am in disagreement with, so plese respond appropriatley, thanks.
240.24(B) states that a grounded conductor must be ran from the supply to the service equipment if the utility company provides a grounded(nuetral) conductor to your premises. 250.24(B)(1) tells us how to size such conductor, which is in accordance with 250.66.
It is my contention that if the service entrance conductors are 500Kcmil, the grounded conductor is to be a 1/0 AWG, in accordance with the table. An engineer's rebuttal to this (by the way, I respect the man's opinions, so don't think otherwise) is that going by the text of section 250.66, if the grounding electrode system consists of a ground ring, ground rod and concrete encased electrode, 2 AWG would be the largest required conductor, citing 250.66(A)(B)and (C). I disagree with this logic becasue 250.24(B)(1) directs you to the table 250.66, and not the text of section 250.66.
The scenario is this: A 400 amp service is installed, and the service is all motor loads (line to line). 500Kcmil phase conductors have been pulled from the CT can to the service equipment, along with a 2 AWG grounded conductor. I asked for a 1/0, citing the above section. The biggest problem that I have is that a 2 AWG condcutor has twice the impedence value of a 1/0 AWG condcutor. Now, on the supply side of the service, I would consider the impedance value of the grounded conductor to be even more important than on the load side of the service, due to it having a greater task in initiating an overcurrent protective device.
Please share your thoughts with me on this, if you have a minute. Thanks in advance.
240.24(B) states that a grounded conductor must be ran from the supply to the service equipment if the utility company provides a grounded(nuetral) conductor to your premises. 250.24(B)(1) tells us how to size such conductor, which is in accordance with 250.66.
It is my contention that if the service entrance conductors are 500Kcmil, the grounded conductor is to be a 1/0 AWG, in accordance with the table. An engineer's rebuttal to this (by the way, I respect the man's opinions, so don't think otherwise) is that going by the text of section 250.66, if the grounding electrode system consists of a ground ring, ground rod and concrete encased electrode, 2 AWG would be the largest required conductor, citing 250.66(A)(B)and (C). I disagree with this logic becasue 250.24(B)(1) directs you to the table 250.66, and not the text of section 250.66.
The scenario is this: A 400 amp service is installed, and the service is all motor loads (line to line). 500Kcmil phase conductors have been pulled from the CT can to the service equipment, along with a 2 AWG grounded conductor. I asked for a 1/0, citing the above section. The biggest problem that I have is that a 2 AWG condcutor has twice the impedence value of a 1/0 AWG condcutor. Now, on the supply side of the service, I would consider the impedance value of the grounded conductor to be even more important than on the load side of the service, due to it having a greater task in initiating an overcurrent protective device.