I installed a 200 amp meter main on the exterior of a house. Landed a #4 copper from the ufer ground to the neutral bar in the meter. I then ran 4/0 SER from the meter main to a 200 amp panel in the home. Inside the meter main, the ground and neutral wire of the SER both land on the neutral bar. In the panel in the house, the neutral wire lands on the neutral bar, but I then drilled and tapped a lug to the case and landed my ground wire there. I then drilled and tapped a ground bar to the case so I could land my grounds on that so I could keep my grounds and neutrals separated in the panel. I know that the main bonding jumper in the meter main can’t rely on the case, but what’s wrong with the grounding wires in the panel using it? The inspector tagged me citing 250.24(C)