I am hoping someone can confirm my understanding is correct (2014 code).
If I have a SDS established at an outdoor, customer owned transformer, with first disconnect at an adjacent building - 250.30(A)(1) exception 2 allows me to bond at the xfmr and at the disconnect, provided no parallel paths are established.
250.30(A)(2) exception says that in this installation, no SSBJ is required. So from the xfmr to the disconnect I could run 3 phase conductors, a grounded conductor in PVC conduit, and bond at each end per 250.102C. Is this correct? It seems as though I should have an EGC as well.
Now - if I am installing per 2011 - the exception to 250.32(A)(2) doesn't exist - so I am required to run a SSBJ sized per 250.102C with the phase and grounded conductors. Is this correct?
Appreciate any input.