As I read 250.30(A)(5) Exception it is permissible to install an appropriately sized system bonding jumper from XO to a ground bar in my transformer and the connect my grounding electrode conductor to that bar.
Another inspector feels that section requires the GEC to connect directly to XO.
Does the connection to the bar meet Code ??
Another inspector feels that section requires the GEC to connect directly to XO.
Does the connection to the bar meet Code ??