zog
 - Charlotte, NC
That is also incorrect. I have purchased SIEMENS switchboard with the 1200A MCB having full range SS adjustable trips. Next?!
1, 2, 3 strikes you are out
Disagree with what? The ASNI defintions? The description that summarizes the main features of equipment built to those standards?
No, I read the definition provided and I still say that a switchboard falls under the term switchgear. Even the first line says "a general term"
Does not each of the popular gear manufacturers have products labeled Switchboard separate from Switchgear? The fact that they have separate products shows they are different units.
Here is what a popular gear rep said about the matter:
In a nutshell, low voltage switchgear is a particular type of assembly that must meet several ANSI standards and tests, and it is tested to UL1558 standards. Required features include Power Circuit breakers, draw-out construction, compartmentalization of the breakers, physical separation between the breakers and the bus, 30 cycle short circuit rating and 100% current rating of the circuit breakers. The testing is much more rigorous than for switchboards.
Switchboards are tested to the UL891 standard. Any freestanding grouping of bus-connected overcurrent protective devices that does not meet the standards of switchgear (above) would be considered a switchboard. Many are very much like panelboards except they are free-standing. Others are similar to switchgear, but don't have all of the features/testing required to meet the switchgear standard. You have to be a lot more specific about the features you want when specifying a switchboard, since there is such a wide offering.
In most cases, switchgear would be more expensive than a switchboard, but if you load up a switchboard with tons of optional features (that might be standard in switchgear), there is very little difference.
That said, switchgear is usually specified for more critical applications - healthcare, continuous industrial processes, data centers, labs, water/wastewater treatment, etc. Many universities also prefer switchgear, especially in buildings where research may be taking place. Some government facilities may also require switchgear, depending on the function and criticality of the building.
...switchgear is ... is tested to UL1558 standards.
Still think Zog and Weressl were being jerks. Have you really never heard of the "gear package" assumed to be short fo switchgear package? And if you have then you should have had the patience to be less dismissive.
I was only asking you to clarify WHAT is your statement "I disagree" refers to? That qualifies - in your book - as being a jerk? WowwStill think Zog and Weressl were being jerks.
You are being carried away by your imagination. The OP is asking how to distinguish a switch gear from a switch board in the field. You are simply playing with IEEE definitions instead of agreeing on a workable consistent method for the OP to distinguish a switch gear from a switch board in the field.Nope. You have made repeated false assertions what constitutes a switchgear. Did you check with the OP if he needed assistance with asking?
Perhaps he bases his conclusion on your responses in general?I was only asking you to clarify WHAT is your statement "I disagree" refers to? That qualifies - in your book - as being a jerk? Woww
That was answered in post #9.You are being carried away by your imagination. The OP is asking how to distinguish a switch gear from a switch board in the field. You are simply playing with IEEE definitions instead of agreeing on a workable consistent method for the OP to distinguish a switch gear from a switch board in the field.
Of course, and I hear grounded conductors called neutrals when they are not.
Point being there is trade slang / common usage and there is the standards. The fact they have different listings is enough for me to accept they are not the same.
No, they are different. Per IEEE:
Switchgear: A general term covering switching and interrupting devices and their combination with associated control, instrumentation, metering, protective and regulating devices with associated interconnections, accessories and supporting structures used primarily in connection with the generation, transmission, distribution and conversion of electric power.
Switchboard: A large single panel, frame or assembly of panels, on which are mounted, on the face or back or both, switches, overcurrent and other protective devices, buses and usually instruments.
Switchgear and switchboard structures are built and tested to different standards: Switchgear to ANSI standard C37.20.1, UL standard 1558, and NEMA standard SG-5, switchboards to NEMA PB-2, and UL-891. Switchgear incorporates only low-voltage power circuit breakers (LVPCB) which conform with ANSI C37.13, NEMA SG-3 and are listed per UL-1066, whereas switchboards may include any combination of protective devices including insulated case (ICCB), molded-case circuit breakers (MCCB) listed per UL-489, fusible switches listed per UL-508 and 977 and power circuit breakers listed to UL-1066.
Best way to know the difference, Switchgear is designed for flexibility and maximum protection, switchgear generally costs 2x what switchboards do. Switchboards are designed to be low cost, usually use cheap MCCB's or ICCB's, and have very few features.
                  Magnum DS / SBI thought in a solidly grounded system the neutral conductor is always connected to grounded so it would be both a grounded conductor and a neutral conductor.
Is that not so?
Neutral Point. The common point on a wye-connection in
a polyphase system or midpoint on a single-phase, 3-wire
system, or midpoint of a single-phase portion of a 3-phase
delta system, or a midpoint of a 3-wire, direct-current system.
Obsessed with so called fault finding and missing out what may help the OP?False again. IEEE IS the definite authority on both, by establishing standards that ARE defining the features that distinguishes each. When these Standards are matured, established in industry practice and accepted by the user community they are elevated to ANSI Standard status.
Perhaps the OP does not want to be bamboozled by a contractor stating a switchboard as a switch gear as the former is less costly.But, I will play along.
What is the practical use 'in the field' to be able to distingush between the two?
Not always
The grounded conductor from corner grounded delta would not be a neutral.
But where is the MCCB shown as used in switchgear?!Yes and no MCCB's are being built that are like 'crossovers' of breakers and suitable for both switchgear AND switchboard applications:
EATON
"Magnum DS / SB
Eaton’s Magnum Low Voltage Power Circuit Breakers are designed for ultimate custom configuration, application flexibility, and performance. Choose Magnum DS breakers for ANSI rated switchgear applications and Magnum SB insulated case breakers for switchboard applications.
They are the same base with slight difference between the DS and SB models. Not interchangeable though...The distinguishing name of Insulated Case.... instead of the Molded Case.... is the clue. The basic feature difference is that one is serviceable ICCB and the other one is rebuildable MCCB.
Technically, an ICCB is like an MCCB, but it is not exactly the same because it is an "insulated case" as opposed to a "molded case". But from a UL listing standpoint, they are considered the same. I think what he is saying (if I may be so bold) is that you can get a "breaker" that uses the same basic construction as a UL1066 Power Breaker, but is UL listed under UL489 and thus is called an ICCB so as to not confuse it with a PB. That means it can only be used in a Switch BOARD, not in Switch GEAR, but you can benefit from some of the same control and protection features in the breakers normally only found in Switch GEAR.But where is the MCCB shown as used in switchgear?!