Isaiah
Senior Member
- Location
- Baton Rouge
- Occupation
- Electrical Inspector
We have a 3MVA, 13.8kV-480V 3PH, 3W solidly grounded power transformer that was shipped from the manufacturer with an XO bushing on 480V side - however there are NO neutral loads. The secondary feeds a 480V switchgear with 14, 500kCMIL per phase and a supply side bonding jumper in each conduit, sized per table 250.102(C)(1).
Construction connected ALL 14 of the supply side bonding jumpers to the XO bushing in the transformer and to the ground buss in the switchgear. QA/QC is saying the SSBJ cannot be connected at the transformer XO because the transformer may read “residual voltage” on the XO. I don’t see this as an issue - but they want to see the SSBJ’s removed from the XO bushing. Thoughts?
Sent from my iPhone using Tapatalk
Construction connected ALL 14 of the supply side bonding jumpers to the XO bushing in the transformer and to the ground buss in the switchgear. QA/QC is saying the SSBJ cannot be connected at the transformer XO because the transformer may read “residual voltage” on the XO. I don’t see this as an issue - but they want to see the SSBJ’s removed from the XO bushing. Thoughts?
Sent from my iPhone using Tapatalk