It’s not 14 conductors; it’s 14 paralleled 500kCMIL per phase. In other words it’s 42 total conductors—3 conductors A,B,C per conduit plus one SSBJ.
Also it wouldn’t make sense to route 14 ungrounded conductors in a single conduit due to correction factors plus the conduit would be enormous at 40% fill. Lol
Sent from my iPhone using Tapatalk
Ok my bad I thought you were asking about SSBJs
500 KCMIL or 500,000 CMIL = 380 i amperes @ 75 deg Celsius x 14 wires per phase = 5,320 i total parallel AMPACITY for secondary
HOWEVER secondary transformer ampacity out put is 3,608.54 i amperes. Your choice of wire would initially seem overkill when resized at 5,320 i but, I believe for continuous loads transformer ampere output and inrush current effect on transformer startup, the 3,608.54 i is multiplied x 1.25 percent = 4,510.64 i ampacity wire needed after considering temperature derating and voltage drop (not calculated)
Sizing secondary transformer ampere output at 3608.54 i x 1.25 for continuous loading conductor sizing = 4,510.67 i ampere conductor needed after derating for temperature and voltage drop. With your paralleled conductors rated for 5,320 i think you look good here?
But what I’m the heck are you powering with that much amperes?