250.30

Merry Christmas

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Just note than an outdoor transformer and/or other equipment is unlikely to be a structure, but there are other sections that require a grounding electrode there.

It appears the only time the SSBJ is required is for indoor XFMR installations.


Sent from my iPhone using Tapatalk
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Or for outdoor transformers where there is a metallic path such as metal conduit.

Or for outdoor transformers where there is a metallic path such as metal conduit.

In our case all the connections from transformer to SWGR are via underground PVC conduit.
Are there any scenarios where a parallel neutral would exist along side a SSBJ?


Sent from my iPhone using Tapatalk
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Off hand I would say if you didn't have a SBJ at the gear you would need to have both a neutral and SSBJ.
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Are all the transformers connected to the same GES at the outdoor location?
Is the respective Service Equipment for each SDS connected to a common GES?

They’ve used a common GES for all XFMRS and SWGR in the form of a grounding ring (buried approx 36” deep) with very few ground rods/test wells and no bonding whatsoever to rebar. Not good design but it’s what we got from the engineering firm.


Sent from my iPhone using Tapatalk
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
They’ve used a common GES for all XFMRS and SWGR in the form of a grounding ring (buried approx 36” deep) with very few ground rods/test wells and no bonding whatsoever to rebar. Not good design but it’s what we got from the engineering firm.


Sent from my iPhone using Tapatalk
IF I understand it, the neutral or grounded conductors will all be in parallel. They are bonded together at both ends.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
If the neutral is bonded at ONE location only what purpose does the GEC serve at both locations?


Sent from my iPhone using Tapatalk
If the neutral is bonded at one location then you need the SSBJ. If the neutral is bonded at both locations, you do not need the SSBJ but you need a SBJ at both locations and a grounding electrode system at both per 250.30(C)
 

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
Say your system bonding jumper is at the transformer and also your GEC/GES.

At the next location the GES would just terminate in the equipment grounding bus and leave the noodle floating in the gear correct?

Just like a sub panel at a remote structure that requires its own grounding electrode system. You would tie It to the grounding bar and float the neutral.

I am obviously not talking as using the exception for parallel paths and grounding neutral at both locations.
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Say your system bonding jumper is at the transformer and also your GEC/GES.

At the next location the GES would just terminate in the equipment grounding bus and leave the noodle floating in the gear correct?

Just like a sub panel at a remote structure that requires its own grounding electrode system. You would tie It to the grounding bar and float the neutral.

I am obviously not talking as using the exception for parallel paths and grounding neutral at both locations.

Art 250 has to be the most confusing in the NEC.
Thanks to all


Sent from my iPhone using Tapatalk
 