I am still wrenching with the correct book answer versus the practablity. Pedestal owned by the power company, 200 amp main. Demarcation is the breaker (line side.) As per 2008 NEC, art 100 and the others, This is the service equipment and the 82 and 1/2 ft of conductors from that breaker to the next panel, (be it a panel on a post, factory ordered panel about to feed a trailer, or a panel on a building, home) Shall be a 4 wire feeder? Yes?(as per 250.32 B) and if so AM I to require service rated equipment at the end of that 4 wire feeder? And will this equipment (service rated) have design for a grounding bar kit to isolate it from the neutral while still grounding the can? The practablity is to have the old three wire service to the structure and derive the GES at that location. (180 linear feet of rebar, versus two ground rods out at the pedestal). Weeeeeeee, that was tough, Oh, and thanks.
 
So whats the question ? is it "should I fallow the code requirement" or is it "should I violate the code requirement ?" :)
 
hep, I mean HELP

hep, I mean HELP

acrwc10 said:
So whats the question ? is it "should I fallow the code requirement" or is it "should I violate the code requirement ?" :)
:mad: Ok, mister, Should I rely on two ground rods as per NEC or should I rely on the linear feet of rebar as my electrode system?
 
Inspectorcliff said:
:mad: Ok, mister, Should I rely on two ground rods as per NEC or should I rely on the linear feet of rebar as my electrode system?

Once you get to the building you still have to connect to the building Uffer so I guess it wouldn't matter.
 
The UL term "Suitable for use as service entrance equipment" means that the ground-neutral bonding provisions are removable, as this equipment can be used in general locations.

The term "Suitable only as service equipment" means that the ground-neutral bonding is factory installed and not removable.
 
ordering

ordering

jim dungar said:
The UL term "Suitable for use as service entrance equipment" means that the ground-neutral bonding provisions are removable, as this equipment can be used in general locations.

The term "Suitable only as service equipment" means that the ground-neutral bonding is factory installed and not removable.
And, I should be able to order either or, correct?
 