transman2
- Brooklet,Ga.
Question,
I have a high mask light pole that has some I.T. equipment mounted about half way up with equipment mounted in a plastic nema box with a metal back plate located at base of pole that we have to run an underground circuit (120V) for a duplex receptacle. Engineering did not put in the spec's for the EC to bond to the ground rod at the pole that is present from the metal back plate.
Correct me if I'm wrong but I know there is an Exception under 250.32(A) saying a ground rod is not required for 1 circuit but 250.50 says that if a electrodes are present per 250.52 (A)(1)-(A)(7) at each building or structure served shall be bonded together to form a grounding system. It also says if none exist, one or more specified in 250.52(A)(4) through (A)(8) shall be installed.
With this being said should 250.50 code, rule over the 1 circuit code in 250.32(A). Sorry for making this so long.