I have an existing building with a 208V service that I would like to backfeed from an outside transformer. To accommodate future mechanical loads we selected a Outdoor 480V service entrance rated switchboard and a 480V to 208V transformer to back-feed the existing 208V service. We are providing the system bonding jumpers per 250.30(A)(1) Exception #2 so that we can re-use the existing feeder and system bonding jumper at the existing switchboard.
In the future, we may bring in a feeder to a 480V switchboard for some mechanical equipment. Per 250.32 we need to connect the equipment grounding conductor to the grounding electrode system of a building served by an outside feeder. My understanding of 250.32 (B) (1) Exception #2 seems to be that we need to connect the EGC to the buildings GEC but by doing so we will create a parallel path in the grounding system. That means we won't be able to use 250.30(A)(1) Exception #2 and would need to run a system bonding jumper between the outside transformer and the existing 208V switchboard.
Is my understanding correct or have I missed something?
I created a diagram in the PDF attached of what I think the requirements of 250.32(B)(1) Exception #2 are just as a visual aid.
In the future, we may bring in a feeder to a 480V switchboard for some mechanical equipment. Per 250.32 we need to connect the equipment grounding conductor to the grounding electrode system of a building served by an outside feeder. My understanding of 250.32 (B) (1) Exception #2 seems to be that we need to connect the EGC to the buildings GEC but by doing so we will create a parallel path in the grounding system. That means we won't be able to use 250.30(A)(1) Exception #2 and would need to run a system bonding jumper between the outside transformer and the existing 208V switchboard.
Is my understanding correct or have I missed something?
I created a diagram in the PDF attached of what I think the requirements of 250.32(B)(1) Exception #2 are just as a visual aid.