I agree with everything except the last line, that the SSBJ is not required between the enclosures if you are in compliance with 250.30(A)(1). But 250.30(A)(1) does not require you to have two system bonding jumpers. Only installing one system bonding jumper is still in compliance with 250.30(A)(1).Or to put it another way.
The main section of 250.30(A)(1) REQUIRES you to have a single system bonding jumper.
The exception #2 to 250.30(A)(1) PERMITS you to have TWO system bonding jumpers, one at each end.
250.30(A)(2) REQUIRES you to have a supply side bonding jumper between the source enclosure and disconnect enclosure.
The exception to 250.30(A)(2) says the SSBJ is not required when you have installed the TWO system bonding jumpers permitted by 250.30(A)(1) exception #2.
(The exact wording) 250.30(A)(1)Exception: A supply-side bonding jumper shall not be required between enclosures for installations made in compliance with 250.32(A)(1), Exception No. 2.
The key difference is that 250.30(A)(1) Exception #2 only kicks in for "a building or structure supplied by feeder from an outdoor separately derived system..."