prawlings1
- Trinity, TX USA
I recently had a detached garage built. The master electrician who supervised the wiring says no grounding electrode is required at the subpanel in the garage. He said that when he installed the electrodes at subpanels in the past that city inspectors made him remove them. With a concrete floor and concrete driveway in place adding a ground electrode will be a lot of work.
The subpanel has no master circuit breaker. The subpanel power comes from a two pole 125 amp circuit breaker located in the main panel of the house. The neutral and ground bus bars in the subpanel are isolated. There is a ground conductor; same size as the power conductors, that connects the ground bus in the main panel to the ground bus in the subpanel.
I am looking at NEC 2011 250.32(B)(1) and exhibit 250.19 and it clearly says that a grounding electrode is required. The electrician says that he thinks the requirement for the ground rod was eliminated in either 2014 or 2017, but I can't find any indication that this is so.
I assume that the ground rod is to improve lightning protection, but I would appreciate someone enlightening me on whether the electrode is still required and if it is why it is necessary.
Thank you
Thank you