I'm stumped looking at Exhibit 250.17 from the Handbook (see below -- I'm pretty sure this is considered fair use).
Now, it was my understanding from 250.32(B) that a new feeder to a separate building needs to include an EGC. That EGC would be landed on the ground bus of the remote building's panel, which would also connect to the remote building's GEC, but would not be bonded to the neutral bus. The only exception to this is for an existing building with a feeder that has a Grounded Conductor but no EGC.
This seems to contradict what is shown in Exhibit 250.17 (above).
The connection from Building 1 to Building 2 looks correct (existing feeder with no EGC and no continuous metallic paths between the two buildings). The Grounded Conductor between Building 1 and Building 2 does double duty as an EGC, and is therefore bonded to the ground bus in Building 2.
The problem I see is with the feeder from Building 2 to Building 3. According to the language of the Code, there ought to be an EGC from the ground bus in Building 2 to the ground bus in Building 3. ... Right? I didn't think it was ever acceptable to use a local electrode for your only equipment grounding connection -- we talk about this all the time, how a ground fault in Building 3 in this scenario likely wouldn't be able to carry enough current to trip even a 15A breaker.
So, is the Handbook Exhibit wrong, or am I missing something?
* This comes from the 2008 Handbook, which is the most current one I have (and the current code cycle where I live). If this is a mistake that has already been corrected in later editions, I apologize for wasting your time with this post.
Now, it was my understanding from 250.32(B) that a new feeder to a separate building needs to include an EGC. That EGC would be landed on the ground bus of the remote building's panel, which would also connect to the remote building's GEC, but would not be bonded to the neutral bus. The only exception to this is for an existing building with a feeder that has a Grounded Conductor but no EGC.
This seems to contradict what is shown in Exhibit 250.17 (above).
The connection from Building 1 to Building 2 looks correct (existing feeder with no EGC and no continuous metallic paths between the two buildings). The Grounded Conductor between Building 1 and Building 2 does double duty as an EGC, and is therefore bonded to the ground bus in Building 2.
The problem I see is with the feeder from Building 2 to Building 3. According to the language of the Code, there ought to be an EGC from the ground bus in Building 2 to the ground bus in Building 3. ... Right? I didn't think it was ever acceptable to use a local electrode for your only equipment grounding connection -- we talk about this all the time, how a ground fault in Building 3 in this scenario likely wouldn't be able to carry enough current to trip even a 15A breaker.
So, is the Handbook Exhibit wrong, or am I missing something?