Open Neutral
Senior Member
- Location
- Inside the Beltway
- Occupation
- Engineer
While waiting for PSE, I got asked about about an existing case. Outbuilding fed with 3 #6's but no fourth wire. Further, it appears the neutral bus is locally grounded...
Now https://iaeimagazine.org/magazine/20...-requirements/ does what I think is a credible job of showing why that's not allowed.
But I got to wondering about alternative solutions. I invite you to tell me how crazy/wrong I am with these.
Now https://iaeimagazine.org/magazine/20...-requirements/ does what I think is a credible job of showing why that's not allowed.
But I got to wondering about alternative solutions. I invite you to tell me how crazy/wrong I am with these.
- If he has only 240VAC tools and lighting, use the three #6 for L1, L1, and ground. (i.e: Is a neutral required if not needed?)
- He could buy a 240:120-0-120 transformer, declare the CT to be the neutral, ground it to the local & ground to main wires. That could handle hand tools.
- Some 240V tools have a 120V control system/DRO, and would have to run off the transformer. Big loads, big transformer, big buck$
- When you call the PoCo with the words "open neutral" {....Never heard of HIM..} they may show up with a large autotransformer with a centertap; they install it at your meter until they can fix your damaged feed. Suppose Joe Bridgeport did the same; it would only need to be sized for his 120V loads.
- So are there reasons each of the above won't work? Will any of them be allowed under the Code?