What code section is that?
And do you know what the reason for it is?
Any winding tap (mid point or not) is not at same potential as the grounded conductor already established back at the source. This makes it an ungrounded conductor and we must provide overcurrent protection on ungrounded conductors.
A center tap on a balanced system is going to be close to same potential as center tap on the source but will vary, but grounding that second neutral point on same system will put current on non current carrying paths between the source and the autotransformer. A grounding transformer basically turns whole system into a grounded system, you would need an ungrounded system to start with.