In the 2005 NEC there is a change to the wording in 250.50. The 2002 NEC had the language "If available on the premises..." NOW the 2005 has changed that to "All grounding electrodes as described... that are present...." Formal interpretation 78-4 to the question "Is it the intent of 250.50 that reinforcing steel, if used in a building footing, must be made available for grounding?" was "No".
With the language from the 2002 code it seems fairly clear that if the reinforcing steel is "available" it shall be made part of the grounding electrode system. My question is; With the new language in the 2005 NEC "All grounding electrodes... that are present.." would the formal interpretation 78-4 still apply? Available and Present are two different terms with two different meanings. I can understand that if the electrician arrives on the job site and the re-bar is already cast in concrete it would not be available but it is still present and the 2005 states that if it is present it shall be part of the grounding electrode system. The exception to 250.50 almost seems to indicate that new construction shall have the reinforcing steel as part of the GES... even if the electrician arrives a little late?
Thoughts and opinions appreciated.
Thanks, Pete
Thanks, Pete