If a metal underground water pipe is used as a grounding electrode per 250.52(A)(1), then would that connection also satisfy the requirement for the bonding of metal water piping per 250.104(A)(1)?
If so, then that would mean the GEC is also serving as the bonding jumper, correct? So then the point of attachment of the GEC/bonding jumper must be accessible?
Also, when 250.52(A)(1) discusses connection within 5 ft of the point of entrance to the building, I assume that distance refers to the length of the pipe, and not the straight-line distance from the point of entrance. Correct?
:?
If so, then that would mean the GEC is also serving as the bonding jumper, correct? So then the point of attachment of the GEC/bonding jumper must be accessible?
Also, when 250.52(A)(1) discusses connection within 5 ft of the point of entrance to the building, I assume that distance refers to the length of the pipe, and not the straight-line distance from the point of entrance. Correct?
:?