Revised Text:
250.52 A (3) Concrete-Encased Electrode. An electrode encased by at least 50 mm (2 in.) of concrete, located horizontally within and near the bottom or vertically, and within that portion of a concrete foundation or footing that is in direct contact with the earth, consisting of at least 6.0 m (20 ft) of one or more bare or zinc galvanized or other electrically conductive coated steel reinforcing bars or rods of not less than 13 mm (? in.) in diameter, or consisting of at least 6.0 m (20 ft) of bare copper conductor not smaller than 4 AWG. Reinforcing bars shall be permitted to be bonded together by the usual steel tie wires or other effective means. Corrosion protection shall be used for any exposed portions of steel reinforcement bars in wet or damp locations. Such corrosion protection shall be hot-dipped zinc galvanized, or approved electrically conductive permanent coating suitable for the conditions, and done prior to the pouring of concrete, and be continuous from a point at least 2” inside the concrete, and extend to the exposed end. Where copper conductor is used as a concrete-encased electrode, exposed portions of the electrode shall comply with 250.64(B), and may be used as a grounding electrode conductor if complying with 250.64(A) through (F). For purposes of 250.68 (A), the exposed portion of the electrode shall be considered part of the concrete-encased electrode for it entire length, if continuous to the qualifying portion(s). Connections to any exposed portion of concrete-encased electrode (copper conductor or reinforcing rods) shall comply with 250.70. Where multiple concrete-encased electrodes are present at a building or structure, it shall be permissible to bond only one into the grounding electrode system.