hurk27
Senior Member
- Location
- Portage, Indiana NEC: 2008
Ok I just read this.
And what I read is when we have a water ground electrode. we add a supplementary ground rod as required by 250.53(D)(2). From what 250.54 says:
Or no resistance requirment?
Why have we been saying it does?
And what I read is when we have a water ground electrode. we add a supplementary ground rod as required by 250.53(D)(2). From what 250.54 says:
This means it is a Supplementary Grounding Electrode and does not have to be bonded to other electrodes?and shall not be required to comply with the electrode bonding requirements of 250.50 or 250.53(C) or the resistance requirements of 250.56
Or no resistance requirment?
Why have we been saying it does?