That is what I am talking about. The few occasions. How you got the idea that I think that is common place is beyond me.
If you have objectionable current entering the structure via the public water supply removing the water line electrode is allowed per 250.6.
If it is leaving the structure via the water lines then you probably have a neutral problem.
Either way current on the water lines should be removed.
Current flow on the water line is commonplace where there is a municipal water system in place. That is a commonplace occurrence in my book.