250.64 (e)

Status
Not open for further replies.

nickelec

Senior Member
Location
US
Hi all, I have a #6 gec running to my water main that is protected by a piece of ferrous RGS that is bonded at both ends my question is as follows.
Can I use a compression fitting or does it have to threaded do attach my migb?


Sent from my SM-G935P using Tapatalk
5b6ac973839b7af10d3898bbdfc7388c.jpg


Sent from my SM-G935P using Tapatalk
 
In my opinion, a rigid metal conduit compression connector is listed for grounding and bonding. The proof will be in the UL White Book Materials Certification Directory. . . So, attaching a grounding insulating bushing to the threads of an RMC compression connector bonds to the RMC itself.
 