Can someone explain how to size the bonding jumper from 1" EMT containing 3/0 GEC to cold water into the service enclosure. The service is 2000 amp, 277/480 volt the service conductors are 6 sets of 500 kcmil. Also, the size at the cold water end, the 3/0 to the 1" EMT. I was told 12.5% of the total area of the phase conductors, per 250.64 (e) & 250.102 (c)
500 kcmil x 6 = 3000 kcmil x 12.5% = 375 so 400 kcmil
So do I need to use 400 kcmil to bond the EMT to the service enclosure and also the EMT to the 3/0 at the cold water.
please correct me if I'm wrong or any advice. Thank you, Chip
500 kcmil x 6 = 3000 kcmil x 12.5% = 375 so 400 kcmil
So do I need to use 400 kcmil to bond the EMT to the service enclosure and also the EMT to the 3/0 at the cold water.
please correct me if I'm wrong or any advice. Thank you, Chip