Re: 250.64B
Also, 250.64(B) says you only need to bury to 12".
I don't believe it has to be. A GEC may be bare copper. If you can direct bury a bare copper wire, is there any reason you can't bury one that happens to have insulation? So what if the insulation breaks down, since a bare wire is allowed.Originally posted by throttlebody:
I would like to add to this if I may.
The conductor being used outside is direct burial rated, correct? I had inspector point this out to me years ago and then It had to start being buried 24" deep before leaving the wall to the rod clamping devices and so forth.
Also, 250.64(B) says you only need to bury to 12".