allenwayne
Senior Member
Re: 250.66
230.D E,but 250.66 say to size to largest,incoming feeder.How do we comply with both
230.D E,but 250.66 say to size to largest,incoming feeder.How do we comply with both
This would not be true if you had an overhead service drop. You need to look at the definitions in Article 100 referring to Service Entrance Conductors. In an overhead system the service entrance conductors would begin at the point where they are attached to the service drop.Originally posted by paul renshaw:
The line side of the meter conductors are irrelevant in this case. They are part of the service lateral, the table says service entrance conductors, which are the ones from the bottom of the meter to the mains in the panels. The meter is the service point and the wires leaving it are the service entrance conductors.
It seems that note #1 would apply to parallel service entrance conductors in an overhead service so this would not apply to your setup.250.66 Size of Alternating-Current Grounding Electrode Conductor.
The size of the grounding electrode conductor of a grounded or ungrounded ac system shall not be less than given in Table 250.66, except as permitted in 250.66(A) through (C).
FPN: See 250.24(C) for size of ac system conductor brought to service equipment.
Table 250.66 Grounding Electrode Conductor for Alternating-Current Systems
Size of Largest Ungrounded Service-Entrance Conductor or Equivalent Area for Parallel Conductorsa (AWG/kcmil) Size of Grounding Electrode Conductor (AWG/kcmil)
Copper Aluminum or Copper-Clad Aluminum Copper Aluminum or Copper-Clad Aluminumb
2 or smaller 1/0 or smaller 8 6
1 or 1/0 2/0 or 3/0 6 4
2/0 or 3/0 4/0 or 250 4 2
Over 3/0 through 350 Over 250 through 500 2 1/0
Over 350 through 600 Over 500 through 900 1/0 3/0
Over 600 through 1100 Over 900 through 1750 2/0 4/0
Over 1100 Over 1750 3/0 250
Notes:
1. Where multiple sets of service-entrance conductors are used as permitted in 230.40, Exception No. 2, the equivalent size of the largest service-entrance conductor shall be determined by the largest sum of the areas of the corresponding conductors of each set.
Note #2 would apply if no service entrance conductors were present at all. This doesn't seem to apply to your installation either since you indeed have service entrance conductors on the load side of the meter.2. Where there are no service-entrance conductors, the grounding electrode conductor size shall be determined by the equivalent size of the largest service-entrance conductor required for the load to be served.
aThis table also applies to the derived conductors of separately derived ac systems.
bSee installation restrictions in 250.64(A).
Why do you say that? The service entrance conductors go all the way to each disconnect whether from a drop or a lateral, they don't stop at the meter. And 230.40 Exception 2 says "service drop or lateral". I think that note 1 is the answer to the poster's question.Originally posted by infinity:
1. Where multiple sets of service-entrance conductors are used as permitted in 230.40, Exception No. 2, the equivalent size of the largest service-entrance conductor shall be determined by the largest sum of the areas of the corresponding conductors of each set.
It seems that note #1 would apply to parallel service entrance conductors in an overhead service so this would not apply to your setup.
Not if you read the definitions of service entrance conductors. Overhead and underground service entrance conductors begin at a different point by the definitions in Article 100.Why do you say that? The service entrance conductors go all the way to each disconnect whether from a drop or a lateral, they don't stop at the meter. And 230.40 Exception 2 says "service drop or lateral". I think that note 1 is the answer to the poster's question.
--------------------
Mark
Kent, WA
This is the problem with 250.66 note #1. The underground conductors that are feeding the meter are not service entrance conductors. By definition in Article 100 they are a service lateral so note #1 does not apply to his installation.Multiple conductors are not parallel conductor as the exception 2 to 230.40 is where one set of serive entrance conductors are split to run to two seperate inclosures.
Service-Entrance Conductors, Underground System. The service conductors between the terminals of the service equipment and the point of connection to the service lateral .
FPN: Where service equipment is located outside the building walls, there may be no service-entrance conductors, or they may be entirely outside the building.
Edited to add that again: A meter is not service equipment. (230.66)Service Lateral. The underground service conductors between the street main, including any risers at a pole or other structure or from transformers, and the first point of connection to the service-entrance conductors in a terminal box or meter or other enclosure, inside or outside the building wall. Where there is no terminal box, meter, or other enclosure, the point of connection is considered to be the point of entrance of the service conductors into the building.