- Occupation
- Licensed Electrician
250.64
(F) Installation to Electrode(s). Grounding electrode
conductor(s) and bonding jumpers interconnecting ground-
ing electrodes shall be installed in accordance with (1), (2),
or (3). The grounding electrode conductor shall be sized for
the largest grounding electrode conductor required among
all the electrodes connected to it.
(1) The grounding electrode conductor shall be permitted
to be run to any convenient grounding electrode avail-
able in the grounding electrode system where the other
electrode(s), if any, is connected by bonding jumpers
that are installed in accordance with 250.53(C).
(F) Installation to Electrode(s). Grounding electrode
conductor(s) and bonding jumpers interconnecting ground-
ing electrodes shall be installed in accordance with (1), (2),
or (3). The grounding electrode conductor shall be sized for
the largest grounding electrode conductor required among
all the electrodes connected to it.
(1) The grounding electrode conductor shall be permitted
to be run to any convenient grounding electrode avail-
able in the grounding electrode system where the other
electrode(s), if any, is connected by bonding jumpers
that are installed in accordance with 250.53(C).