How do you interpret this section?
For a grounding electrode I am under the impression that you can attach to the interior metal water piping anywhere in the building and then bond around the water meter.
To me this section 250.68(C) (1) says if you are going to use the metal water piping as a conductor to interconnect electrodes of the grounding electrode system then you must attach your grounding electrode conductor within 5 feet of the underground metal water pipe entering the building.
It does not mean you have to connect your grounding electrode conductor within 5 feet of the underground water pipe entering the building if you are just going to the meatal underground water pipe?
For a grounding electrode I am under the impression that you can attach to the interior metal water piping anywhere in the building and then bond around the water meter.
To me this section 250.68(C) (1) says if you are going to use the metal water piping as a conductor to interconnect electrodes of the grounding electrode system then you must attach your grounding electrode conductor within 5 feet of the underground metal water pipe entering the building.
It does not mean you have to connect your grounding electrode conductor within 5 feet of the underground water pipe entering the building if you are just going to the meatal underground water pipe?