ryan_618
- Salt Lake City, Utah
250.80 Service Raceways and Enclosures.
Metal enclosures and raceways for service conductors and equipment shall be grounded.
Exception: A metal elbow that is installed in an underground installation of rigid nonmetallic conduit and is isolated from possible contact by a minimum cover of 450 mm (18 in.) to any part of the elbow shall not be required to be grounded.
Change to read:
Exception: A metal elbow shall not be required to be grounded where it is installed in a nonmetallic raceway and is isolated from possible contact by a minimum cover of 450 mm (18 in.) to any part of the elbow or is encased in not less than 50 mm (2 in.) of concrete.
Substantiation: This change makes the exception to 250.80 mirror exception number three to section 250.86. The protection afforded by 2 inches of concrete encasement should be considered as equivalent to 18 inches of earth cover. Section 230.6 seems to agree with the concept, when it considers 18 inches of earth cover or 2 inches of concrete encasement suitable to consider service conductors ?outside of the building?.
Change to read: