250.97??

Status
Not open for further replies.

jes25

Senior Member
Location
Midwest
Occupation
Electrician
The way I am understanding bonding for over 250V is that you need to use bonding bushing around ringed KO's. We are refered to 250.92 which only requires assured bonding on 1 end of the raceway.

So if I ran a piece of MC from a panel with ringed KO's to a box with KO's listed for grounding (see exception 250.97) would I need the bonding bushing on the panel end? Or is the raceway code complianlty bonded via the listed KO's on the box ends?

I see a lot of guys installing a ground wire for 480/277 circuits but not using a bonding bushing to bond the raceway itself I see this as a violation anyone agree?
 
Unless the MC jacket were listed as an EGC (only some very new MC cable is) it wouldn't require a bonding bushing if the KO's were eccentric or concentric and not listed for bonding over 250 volts.
 
infinity said:
Unless the MC jacket were listed as an EGC (only some very new MC cable is) ...

Not to thread hi-jack....but...

Is the MC that is listed as EGC disquinshable (sp?) from the typical MC by some means AFTER it is installed? ie, a green strip or something?
 
celtic said:
Not to thread hi-jack....but...

Is the MC that is listed as EGC disquinshable (sp?) from the typical MC by some means AFTER it is installed? ie, a green strip or something?


Good question. I've never seen it. Still see alot of the blue stuff.
 
So the intent of 250.97 is to assure the connected equipment (ie: light fixture) is connected to a solid EGC, and not to bond the raceway itself. Or both?

Consider the EMT pipe run with ringed KO's. If I install a EGC inside the pipe do I not have to bond it the pipe itself, to assure the raceway is bonded.


To clarify things here, I understand the required use of a bonding jumper and bonding bushing when using the EMT as the the EGC. These questions are relating to bonding the raceways when a EGC is installed in addtion to the EMT.
 
Last edited:
Consider the EMT pipe run with ringed KO's. If I install a EGC inside the pipe do I not have to bond it the pipe itself, to assure the raceway is bonded.


IMO this section is rather vague. Here's what Mike Holt has to say:


"Metal raceways or cables, containing 277v or 480 v circuits, terminating at ringed knockouts must be bonded to the metal enclosure with a bonding jumper sized in accordance with table 250.122...."
 
infinity said:
IMO this section is rather vague.

I think it is vague as well. I spent about 20 minutes analyzing every word of 250.97 and using the mike holt book.

Around here standard operating procedure is to install a ground wire if you have 277/480 circuits with no bonding bushings involved.

If the intent here is to bond the raceways then I think you would need the bonding bushings even on MC wiring methods to bond the metal cable sheath. Any inspectors see it like me?

I hope I am wrong.
 