I need to upsize a wire for voltage drop. I need to use 250 kcmil AL and it is going into a 200 amp GE breaker. Is there some kind of adapter or lug that will accomplish this? 4/0 is the largest size wire listed.
 
There is a an adaptor for this purpose....can't find my link at the moment.....please standy by...
 
Here's the one Dez posted:

CPM.gif
 
I would expect that there is an optional lug from GE that can be field installed on your breaker to accommodate the larger wire size.
Don
 