VirutalElectrician
- Mpls, MN
- Sparky - Trying to be retired
But it'll be lighter on the way out!Sux when you need to pull only 80 feet but gotta drag a whole spool inside
I haven't seen a box of NM since the 80's.We mostly used boxes but there was a time when we were doing many new homes so we switched to reels. To be honest, the reels were a nuisance for me-- heavy and hard to unreel. We went back to 250' boxes.
The 250 I'm talking about is RomexWhere do you guys even find 250' thhn rolls, all we have here is 25, 100, 500, 1000, 2500. 250 would be a nice middle ground bewteen 500 and 100.
I think my #4 smaller reel is like a 315 or something wierdWhere do you guys even find 250' thhn rolls, all we have here is 25, 100, 500, 1000, 2500. 250 would be a nice middle ground bewteen 500 and 100.
My issue of the 250's on whole house wiring is the amount of shorts at end of rolls, will get stuck with a bunch of 6-11ft pieces. may get the same on the 100ft spool but only one rather than 4 such pieces. Only issue of the 1000ft spool on smaller jobs is "How much did I use on this job?" Was consistently shorting myself on billing so got a measure meter so I can bill out exact length pulled from spool.I've wired new homes as small as 800 square feet and as large as 15,000 square feet. And I've used 1,000' spools on each, as well as 250' rolls on each.
I much preferred 250' rolls
Just so much easier tool take into a house and up a flight of stairs
I find little value in it. It's about 2.5x the cost of 12/2. Then you have to find a box somewhere to split out the circuits.True on weight issue of spools but have a hand truck spool rack. Another thing on the rolls is getting more twisting of wire during dispensing vs a 1000ft spool.
Anyone using the 12-2-2 for home runs?
I like it from basement to second floor runs to get 2 individual circuits in one pull. No shared neutral so no handle tie.
Better use of it I've seen is 14 2 2 that cable could be going to a far side of the house lighting circuit and take care of a lot without being a lot of box fillThis has always bothered me on NM cable. We've had footage marks on network cable for decades. Why can't we get it on NM?
I'm getting it at 2.25x cost, Anyway, it is either 2 pulls of 12/2 or 1 pull of 12/2/2 so effective cost is only 25% more for the wire. So cost to customer even with markup is about for me $30 less, labor included on a 75ft pull, using 12/2/2 vs 2 pulls of 12/2.I find little value in it. It's about 2.5x the cost of 12/2. Then you have to find a box somewhere to split out the circuits.
I'll roll out multiple home, runs across the floor and cut them to length and add about 20 or 25 ft to each one. Enough extra that I can use it somewhere else.1 pull of ##/2/2 vs making 2 pulls of 12 or 14/2, to get home runs on an upgrade or remodel. Have also used when got new construction addition over crawl space, only crawl thru one time vs multiple trips thru.
I want to make sure I'm not a moron here. in Table 310.15(B)(16) (2017 NEC) AWG14 THHN has a 20A rating up to 75°C. Why not use it with a 20A breaker?We had boxes of #12 & 14 THW & maybe TW wire in 500' boxes in the late 1960's . Luckily a wire company salesman stopped by think it was 1967 and gave us samples of THHN/THWN ( guessing it was dual rated back then ). When we called our electrical supply house to place an order were told no such thing as THHN insulation but we persisted. Owner of the supply house ripped the wire company of not informing them first on new products. Only bad thing too many electricians found that #14 copper THHN THWN conductors were rated for 20 amps ( guessing at 90 C table ) so they feed it with 20 amp breakers. Luckily the very talented inspectors picked that mistake up rather quickly and stopped that code violation.
Due to 240.4(D).I want to make sure I'm not a moron here. in Table 310.15(B)(16) (2017 NEC) AWG14 THHN has a 20A rating up to 75°C. Why not use it with a 20A breaker?
The #14 AWG THHN can be used @ 75° C, that's 20 amps for applications that fall under 240.4(E) or (G) for example motors or HVAC applications.Ah yes... 204.4(D)(3) says AWG14 cannot go over 15A. So what is the meaning of the 20A rating of THHN at AWG 14 in Table 310.15(B)(16)? Is it only theoretically permitted, but not practically permitted. Or maybe useful for calculating ampacity of conductors in parallel?
