When I returned to begin the hunt for the problem, we started with a feeder conduit wiring j-box due to a high resistance to ground reading from the de energized panel neutral and water pipe in the apartment. Crawled through the nasty attic opened the j-box and found nothing. I crawled out whet down to my service van for a drink of water and did a little more testing at the meter stack . I was sure I would find nothing but did it anyway. I clamped the conduit that had current on it and it was still there of course but it was only 4 amps at this time. At this time I noticed the main was not properly secured to the 1880 brick building and was putting diagonal torque on the connection busses.
Tested neutral to main line voltage in bank 1 meter stack had perfect balance then I tested neutral in bank 2 to main line voltage and this time I had 121v A phase and 123v B phase.
Same one bank 3 meter stack. Bingo light went on just like in the cartoons!
Continued test from bank 2 to line and pushed slightly on the main enclosure and it went back to balanced voltage. Called LPC power they came out and removed meters so I could access buss connection bolts and they were all loose in both section 1 and 2. In my opinion they were never tightened during original installation orver 30 years ago. I got 9 turns out of every one on both sections re-energize gear all issues of unbalanced voltage and conduit current and ground current were solved. Due to observations of arching on A and B phase we have a meter bank and main to replace some time in the near future. Just wanted to say, sometimes even when all things point to a bad piece of service bussing and you cannot find anything wrong with meter testing look around and if something in the install isn't look right just give it a little tug or a shove you may be surprised what you will find after that.
Temporarily adding more load also makes some problems reveal themselves better. (sometimes best to not do so with the regular load connected though, especially if you are tracking down a suspected bad neutral issue).
 
Status
Not open for further replies.
Top