I am having trouble with this issue. The piece of equipment discussed below is not a motor and doesn't have overload protection.
Piece of equipment with nameplate value of 17A. Continuous operation, so this equates to 21.25A. The next size breaker is 25A. However, the piece of equipment comes with a standard 5-20P so I have it being connected to a typical 5-20R.
Is this allowed or does the 25A breaker not protect the receptacle?
Piece of equipment with nameplate value of 17A. Continuous operation, so this equates to 21.25A. The next size breaker is 25A. However, the piece of equipment comes with a standard 5-20P so I have it being connected to a typical 5-20R.
Is this allowed or does the 25A breaker not protect the receptacle?