Most conductors can handle inrush with no issue.
A bare copper wire about thick as human hair, held in liquid nitrogen under pressure, can handle thousands of continuous amps, just takes a very long time for the liquid to vaporize and copper heats and melts.
Using 125% rule does not make much sense if the main idea is that the OCPD should not be any bigger than the rated ampacity of the wire. A motor that has inrush of 28A but runs full load at say just 16A can perhaps still pose an issue, like you run #12 wire and use a 25A ocpd, what happens when the load goes south and begins to run 21A after startup? OCPD does not care, but the #12 does (using NEC rules, etc).