When did 277/480 come into existence? Or 277 volt lighting?
They mention 440 volt delta and 254 volt Y-connected motors in this short piece from 1910:
https://books.google.com/books?id=b...ge&q=254 volts electric journal delta&f=false
At the link below starting on pg. 556 they discuss the types of electric service in Oakland, CA in 1910. It includes 440V and interestingly mentions some residential customers with 220V but no 110V. Also 7-1/2 amp constant current for the series arc lamps in the city . I wonder what the open circuit voltage was on those circuits?
https://books.google.com/books?id=y...conditions at oakland, california 556&f=false
I'm guessing that 440 volts migrated up to 480V in a comparable time frame as 110V moved up to 120V (same percentage increase and maintaining same 4:1 ratio).
I think Wye in general was not as common back then. I would guess 120/208 also came a bit later just like 277/480?
Same here, and that is what interests me.
It seems everything other than 120/240 single phase was sealed off from earth and the remnants are its still reflected in code to this day.
Wasn't October 1959? I think it's the seventieth anniversary and we are all missing it because it's football season.
Just assuming from what I have seen, which is certainly limited in scope and geographic area, there were not many Wye systems before the early 70's. Seems three phase was often ungrounded delta without ground detectors hmy:
There was definitely a big push toward grounded systems at some point (both in distribution and premis). Although grounded distribution cuts costs a bit, I still think part of it was myth based, grounded=better=safer
I'd say so, but remember that many ungrounded systems were just operating with a standing ground fault. Those that ran into transients faults sometimes encountered insulation damage.
I can't find it, but many years ago I read a paper toughting that 277/480 came into existence because of the advantages associated with 277 volt lighting circuits.
Yeah no doubt. An old building I worked in had a 600V ungrounded service. It had a fault and who knows how long it had been like that, could have been decades. I finally did find it when I was re-routing the elevator circuit into a transformer after upgrading the service to 120/208.
That makes sense. That would make it a lot more efficient for larger buildings to take 277/480 without need to transform most of the lighting. I really hate our low voltages. Hate 208. Even 240 is too low. Like the way Europe does it with 230/400 - except I do like our 60hz
Another question: What happened to 600v? was that a fad that faded out? Lots of the mills in New England were 600. Pretty much never see 600 anymore.
Just assuming from what I have seen, which is certainly limited in scope and geographic area, there were not many Wye systems before the early 70's. Seems three phase was often ungrounded delta without ground detectors hmy:
At least as far back as the 1950's, Square D was selling ML-2 and NY1B circuit breakers for use on 277V. In 1958, the Square D QO line was listed as suitable on 120/208VAC 3PH 4W.
Do you know when the QO line came out?
Talking of odd voltages and this is one I never did find the reason for. We used either 433V or 550V, the plant this was on had all German equipment which at that time normally would be 415V.
A 440V transformer would be a special order, I don’t know why?
At least as far back as the 1950's, Square D was selling ML-2 and NY1B circuit breakers for use on 277V. In 1958, the Square D QO line was listed as suitable on 120/208VAC 3PH 4W.
Utility transformers often have a slightly odd voltage. They are often designed to supply not the nominal utilisation voltage, but a voltage at the upper end of the permitted tolerance band, so as to allow for voltage drop between the transformer and the load..