277V 2-WIRE PANEL

SGTARMY

Member
Location
LA
Occupation
Electrical
Do does any manufacture provide such panel? Or can I use a 1 phase panel 3 wire and just just a single phase and mark off the second panel.
 
Welcome to the forum.

Are looking for one line and the neutral, or two lines and the neutral?
 
Welcome to the forum.

Are looking for one line and the neutral, or two lines and the neutral?
The title says 2-wire the OP says 3-wire? :unsure:
3-wire would be 480 unless they're counting the EGC.
 
Last edited:
sorry 2-wire one hot and one neutral. I have an inverter that’s that is only has a 277V output.
 
It’s a sizable inverter, has around 12 circuits. The output feed was suppose to be 480/277 trying to see what options there is.
 
It’s a sizable inverter, has around 12 circuits. The output feed was suppose to be 480/277 trying to see what options there is.
I didn't realize you had multiple circuits. I understand a lot of this, but have little experience.

Do you mean multiple DC or AC circuits? I doubt they all can or should be on one phase.

It sounds like a typical 3ph 480Y/277v feeder and panel might be appropriate.
 