We are building a manufacturing cell which is to have a small overhead fan and 2 doors served by 3 way switching for the overhead fan.
Customer requirements are work is done to NEC.
Conductors entering the overhead fan box = 14 including the grounds.
6 Conductors THHN120V in and out. (powering other lights)
4 Conductors THHN serving the 1st switch.
4 Conductors THHN serving the 2nd switch
14 Conductors x 2.0 cubic inches = 28 cubic inch box needed.
I can not find a metal fan box (one pc) that is bigger then 25 cubic inches.
Thanks for your time, CD