I am working on a design/build project for a long-time customer of ours. They are looking for a cost effective solution (isn?t everyone) to powering some new plant equipment. Here?s what I want to do.
Install a 2MVA 4800V-480V Delta-Delta Transformer fed from an existing GE Magna-Blast breaker (I will set the overloads after the coordination study) to feed their two pieces of 480V equipment. The secondary of the transformer does not have a Center Tap, so no potential of High-Leg voltage. The 480V switchgear will consist of (1) 2500A MLO 480V 3-Phase 3-Wire Switchboard w/ 1 - 1000A 3P Fusible Switch and 1 ? 1200A 3P Fusible Switch.
Can I simply take the ?B? corner of the secondary to ground and then run the 3 phase conductors to the 480V Switchboard? Then P-P Voltages would be 480V and P-G voltages would be A-G 480V, B-G 0V and C-G 480V. Because this is a delta secondary then I wouldn?t need GFI protection either, correct?
I want to look at this as their first option because I can get a great deal on the Delta-Delta transformer and the fact I won?t have to have a GFI on the secondary. I am going to verify that the equipment can operate at this corner-grounded voltage.
I appreciate any and all feedback before I take this idea to our Principle for his blessing to move forward. I?d like to know if I?m on the right track before I go any further.
Install a 2MVA 4800V-480V Delta-Delta Transformer fed from an existing GE Magna-Blast breaker (I will set the overloads after the coordination study) to feed their two pieces of 480V equipment. The secondary of the transformer does not have a Center Tap, so no potential of High-Leg voltage. The 480V switchgear will consist of (1) 2500A MLO 480V 3-Phase 3-Wire Switchboard w/ 1 - 1000A 3P Fusible Switch and 1 ? 1200A 3P Fusible Switch.
Can I simply take the ?B? corner of the secondary to ground and then run the 3 phase conductors to the 480V Switchboard? Then P-P Voltages would be 480V and P-G voltages would be A-G 480V, B-G 0V and C-G 480V. Because this is a delta secondary then I wouldn?t need GFI protection either, correct?
I want to look at this as their first option because I can get a great deal on the Delta-Delta transformer and the fact I won?t have to have a GFI on the secondary. I am going to verify that the equipment can operate at this corner-grounded voltage.
I appreciate any and all feedback before I take this idea to our Principle for his blessing to move forward. I?d like to know if I?m on the right track before I go any further.