My questioning has nothing to do with grade level, it has to do with intended use of the receptacle in question.
Lets look at 210.8 and consider the probable loads.
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">bathrooms - hair dryers, curling irons, shavers, etc...
garages - hand tools, power tools, lawn equipment, etc...
outdoors - yard tools, trimmers, cutters, extension cords, etc...
kitchens - blenders, mixers, toasters, etc..
rooftops - hand tools, extension cords, etc..</font>
<font size="2" face="Verdana, Helvetica, sans-serif">
So now, consider a second floor patio or balcony. What loads similar to the ones above are likely to be used there? All those above are personal and handheld in nature. I doubt these types of utilization equipment will be used in the location of a second floor or higher outdoor location.
I'm not arguing that the code doesn't apply there, I agree it does. I just question the issue for the sake of discussion. I also don't like exceptions on top of exceptions, and feel extra safety is better than minimal safety. But really, if outdoors is so important for GFCI protection, than why doesn't the NEC require non-dwelling outdoor receptacles to be GFCI protected?