They were having motor issue. Pool pump in a gym. Pump was not the issue.
The maintenance team said they replaced two pump and now a third. The breaker would rest after each replacement.
When looking at the pic also look for other issues. Check out the handle of the common trip breaks below the one I had out.
For a temp repair we moved the pump to a new spot and also relocated the load across from it until other repairs could be made.
Reversing contactor for a commercial disposal.
If would reverse and was going into lock rotor.
Maintenance got it to work by using a screw driver jamming in the forward contactor.
The reverse contactor has a welded set of contacts.
You can see the marks in the pick.
Plus he showed me. I said don't do that again.
Need to look for full pic. We reworked the whole box and install thermal over load protection.
It was hot wired.
When I run across these items the first thing I ask the apprentice to do is take a good long hard visual insp.
Ask your your self what's missing.
In this case no overload protection.
The motor was a three phase with no built in thermal protection.
I ask them to draw these out. Simply using what's required for this motor circuit.
You will also notice the inter locking control wireing keep it from running with out a screw driver jamming the forward contactor in.
The inter locking had a reversing control circuit with a timer so it would change direction after each cycle run.
Fun stuff.