2p 20a breaker

Status
Not open for further replies.

templdl

Senior Member
Location
Wisconsin
Is it against code to feed a single pole 20a duplex with a 2pole breaker?

If you had an existing spare 20a2p breaker and wanted to use it to supply power to a single20a branch circuit to feed a duplex receptacle using one pole of the breaker I can find no code violation in order to do so. You could even use the other pole to feed an additional circuit. The only issue would be is if you had an event happen of one pole that would cause a trip it would cause the other pole to trip which could be judged as a poor design.
 