Can you use a 3Ǿ transformer for single Ǿ? Meaning fed from single Ǿ and feeding a single Ǿ load.
To expand on Steve66... Technically, a winding of a 480 to 208/120 Delta to Wye transformer has 4 to 1 winding ratio. so each coil steps 480 to 120 and the connection points on the secondary would have to be from say A to B on the primary, but A or B to neutral on the secondary.Not a dumb question, and maybe not as simple as it would first seem. I was tempted to say sure, no problem.
But assuming it's a delta to wye, there is probably no connection to the 3 delta point.
1st winding will see normal L-L voltage, but then the other two windings will be in series across the L-L voltage. So their voltage should be too low, and maybe only half of what they should be.
Then we have to think about the coils of wire, and the magnetic flux, and what voltages that produces on the secondary windings, and maybe even how that reflects back to the primary windings.
So offhand, it doesn't sound like a good idea, and I could understand why it might die early (if it works at all).
Now if it was a Y to Y, I don't think it would be a problem.
It is a delta-delta transformer.
So two windings would be used, giving 30kVA?Most three phase transformers are nothing more than 3 single phase transformers sharing a common core. Your 45kVA unit could handle roughly 15kVA using a single winding. The nameplate limit is 54A on the primary.
No.So two windings would be used, giving 30kVA?
Then I don't think this transformer will work. I don't know the actual load, but it is fused at 100A.No.
You use only 1 winding set like H1-H2 in and X1-X2 out.
Any other connection would require an analysis of the magnetic circuit and is typically discouraged.