There is another option: use three X-10 transmitters in this box. They'd only require a single 14-2 supply, so the 1.5"-deep boxes would be more than deep enough.
Three devices = 6 conductors
One 14/2 = 3 conductors
Total = 9 @ 2 cu.in. = 18 cu.in. box
With the 22.5 cu.in. volume of the 1.5"-deep gangables I first mentioned, you could add as many as two additional conductors if necessary.
Three devices = 6 conductors
One 14/2 = 3 conductors
Total = 9 @ 2 cu.in. = 18 cu.in. box
With the 22.5 cu.in. volume of the 1.5"-deep gangables I first mentioned, you could add as many as two additional conductors if necessary.