chevyx92
Senior Member
- Location
- VA BCH, VA
Started a job today in a mall, where there is an existing 3" emt conduit stubbed into the unit where I am working. The run goes all the way back to the switchgear in the electrical room. The run is over 650 ft. with a pull box at about the 400' mark that has (2) 90's and (1) 45. I am having no luck sucking a jet line through. I am using a 5 hp shop vac and a field made head to suck through. I barely have any suction to get that line through. I have done this many times, not on a 3" pipe before but.. am I doing something wrong here? All fitting are set screw type. Do I need a bigger vacuum?