I have read a lot about 200v compressors and before I move forward with purchasing a transformer to make this work I wanted to double check if anyone knows if I can make this work on my current shops set up.
Service:
120/240 3 phase with a delta high leg
any advice would be great.
Well said that man.Spend your money on a 240V motor. Don't spend money on a transformer. It's way easier to change the motor than it is to buy and wire up a buck boost.
You have to wonder...........If it is new - why didn't they order the correct version for what you have for supply voltage in the first place?
You have to wonder...........
I can't read much either on his drawing - gets too blurry when you enlarge it. But looks like the thing possibly can be configured for different voltages. Sure looks like motor is capable of being configured for 480 volts, if so I see it being suitable for 240 volts before it will be rated for 208 volts. After that control transformer may be all that is left that needs attention.The OP is the customer and he has not ordered anything. It is a personal project he is thinking about for his shop. OP is an EC.
OK. Why even think about something that is not matched to his supply voltage?The OP is the customer and he has not ordered anything. It is a personal project he is thinking about for his shop. OP is an EC.
He probably got a steal on whatever it is he ended up with - now has to make it work. It was likely connected to a 208 volt system before, is possible it can be configured for 240 volt system. Motor itself will likely be fine on 240 volts even if only labeled for a 208 system, that leaves you with lesser expensive item of a control transformer that may need changed if it can't be configured for 240 volts input. I would run the motor on 240 until it burns up - probably will be a long time before that happens anyway.OK. Why even think about something that is not matched to his supply voltage?
I'm simply asking the why. It isn't an issue we routinely come across here. And even if it was a non-standard voltage, we knew that going in and designed accordingly.
It seems to me that this analogous to the OP's situation. He knows the voltage his shop has. So why even consider a piece of kit that is a mismatch and may require extra kit to make it match?
To the OP:
Is the problem that you can't get a 240V 3ph compressor? Or are they too expensive?
He probably got a steal on whatever it is he ended up with - now has to make it work. It was likely connected to a 208 volt system before, is possible it can be configured for 240 volt system. Motor itself will likely be fine on 240 volts even if only labeled for a 208 system, that leaves you with lesser expensive item of a control transformer that may need changed if it can't be configured for 240 volts input. I would run the motor on 240 until it burns up - probably will be a long time before that happens anyway.
My guess it was a auction find, a local scrapyard with multiple locations bought a I-R compressor with a 200V single voltage motor at auction, (to my knowledge I-R will not supply a tri-volt 200-230/460V motor to use on 208V, only a 200V motor), but the voltage at that yard is 120/240V 3Ø, someone just wired it & plumbed it as-is.
The question to the OP remains why go down that route?the dwg shows a 440-460 or 220-230 motor?
a 15% buck xfmr should do it
240-208 https://www.schneider-electric.us/en/faqs/FA91925/
what is fla at 200 vac?
The question to the OP remains why go down that route?
As I said to Dave the Rave, it's more losses. Also, it's at least another half a dozen points of potential system failure.
Makes no sense unless there is information that has not been shared.
As I said to Dave the Rave,,,,,,.
Um....no safe answer to that................Are you implying that ActionMan is a raving lunatic?
If so, I agree.
I think the thin mountain air might be partially responsible.
Sound advice as ever.Before doing anything, go read the actual motor nameplate.