There is one oddity in the mix. That is 3 phase motors for the 120/208 volt power systems. For example,
if the power system were to be 208 volts minus 5% (approximately 198 volts) and you were using a 230
volt motor, then the 230 volt motor could only go down to 207 volts (-10%) without being in trouble.
There would be a discrepancy between the 198 volt low range of the system voltage, and the 207 lowest
operating voltage of a 230 volt motor, this could spell trouble. So how can this be addressed?
There are two ways that motor manufacturers have faced up to the problem. The first is to provide
motors rated for 200 volts that can operate successfully down to 180 volts, or up to 220 volts. This is
an adequate margin to cover the normal range of voltages that could be expected on a 120/208 volt
system. But using this approach exclusively would mean that the complete inventory of motors in all
sizes, enclosures, mechanical configurations, etc. would have to be duplicated to handle the motor
requirements for the 120/208 volt power systems. This would be very expensive and cumbersome,
especially with the wide variety of small motors (under 10 HP) that exist.
So most motor manufacturers have taken a different approach to handling these smaller motors. This
approach is that by using a somewhat more conservative design on the 230 volt motors it is possible to
create a 3 phase, tri-voltage motor with voltage ratings of 208-230/460. With this approach the 230 volt
winding ( and connection diagram) is used on the 208 volt power system. When this approach is taken
the motor manufacturer is essentially saying that this motor can be successfully operated on voltages as
low as 208 minus 10% or 187 volts. This approach usually works very well since 208 volt power systems
are normally used in small buildings with relatively short distances between the incoming power service
and the utilization equipment. These short runs tend to make 208 volt power systems quite stable so that
the limit of the motor’s low voltage capability is seldom tested.
On motors larger than 10 HP the 200 volt motor is generally the best choice, but in many situations 230
volt motors are frequently and successfully applied on the 208 volt systems. In some cases a derate table
is provided for the “low voltage” situation. In other cases the motor service factor may be reduced from
1.15 down to 1.0 when it is applied to a 208 volt power system.