Do all ATSs sense the neutral lug (phase to neutral monitoring)?
Do all ATSs sense the neutral lug (phase to neutral monitoring)?
Too general of a question, maybe one has a three phase three wire delta supply - no neutral to monitor even if you wanted to:happyyes:Do all ATSs sense the neutral lug (phase to neutral monitoring)?
Too general of a question, maybe one has a three phase three wire delta supply - no neutral to monitor even if you wanted to:happyyes:
Do all ATSs sense the neutral lug (phase to neutral monitoring)?
Well, the ASCO 7000 ATS's will work on 3 wire systems.
From a set of shop drawings I have, it lists Voltage 3 Phase (3 or 4 wire), and then it lists all the available voltages.
This one just happens to be going on a 3 phase Wye system, with no neutral ran to the ATS or MCC.
But is the ATS going on the primary side of this transformer? If not, and its going on the 120/208V system, you should have a neutral.
My experience with all ATS manufacturers: the answer is no. I can not think of one brand that senses phase to neutral voltage.
What would be the reason? Whether it is a 3-wire Delta or 4-wire Wye monitoring the 3 phase to phase voltages will indicate whether the source is good or not for transfer of the load. Your typical ATS always senses the 3-phases on the utility source. This is because of the danger of single phasing from the utility causing damage to the load. The sensing on the emergency source varies between 3-phase and single phase depending on the age and manufacturer of the unit. Most newer microprocessor controllers (GE-Zenith MX-150, MX-250, MX350) give you the option of selecting 3-phase or 1-phase voltage sensing for the emer source.
Ok, I see what your question is now and you have a valid point. I noticed this on some ASCO dwgs I have.The Kohler schematics show wiring from the neutral lug/buss over to the electronic control. I have seen the actual ATS in person and I can confirm this.
http://www.kohlerpower.com/onlinecatalog/pdf/gm46266.pdf
As well as the spec sheets say under LCD display "line to neutral voltage" (page two)
http://www.kohlerpower.com/onlinecatalog/pdf/g11108.pdf
Not saying your wrong but its confusing me:dunce:
Ok, I see what your question is now and you have a valid point. I noticed this on some ASCO dwgs I have.
You are asking what do you connect to the P1-22 and P1-23 inputs on the PSB? I need some time to look into this but it would seem to me that there would be programming settings in the Setup menu where you would choose the type of system you are installing the ATS on; 3-wire Delta or 4-wire Wye. If you choose Delta then the phase to neutral voltage setting you now see will disappear and you would not connect anything to terms P1-22 or P1-13. It would be much the same way as when you are installing power meters or protective relays for the first time. I would check the Setup menu after you power up the controller. It is set for 4-wire and you need to change it to 3-wire (Delta) to solve your problem. You will not do any damage by not connecting any wires to those terminals, it just your readings will not be correct until you make that change to Delta.
We need the controller programming manual for this information.
Yup! You got it! I don't have the manual for programing, but its those connections from the neutral buss to the control PSB that throw me off. In my mind (Im guessing) the control has a need for a neutral, either for electronic power, sensing or both. I never stopped to think about it until now when I realized the ATS had this connection. I went looking through the Kohler and ASCO specs and could find anything in the ordering info asking for "4 wire" or "3 wire". Only solid and switched neutral, thinking solid neutral was just a buss kit with no connection to the electronic control.
Your explanation does make sense if that's the case. Any way to find out?
Do all ATSs sense the neutral lug (phase to neutral monitoring)?
I have installed many of these and I can tell you for a fact that the neutrals are normally connected separately and not monitored for amperage.
See my post #10.
Amperage has nothing to do with voltage sensing on ATS source voltages.
Please read the posts and educate yourself before you rattle off jibberish.
Ok then, simple answer is no.
The Guru answer is three posts long and includes an attachment with the same answer.